Hi Guys. I'm gaffering a shoot in a big old country home which itself runs off a 7.5kVA generator. I want to use a 1.2k HMI to try and keep power to a minimum so first question is do I actually need a synchronising crystal generator to ensure I don't "hurt" "blow" the light.

 

This will also be my first time hiring a genny and so I don't know what the socket options are. All the lights I'm hiring use the standard edison UK 3 pin (I think) and so I don't know if the genny has the same output sockets or if I will need some sort of adapter?

 

Cheers,

Chris.

Link to comment
Share on other sites

Ok. i miss something
the generator will power you and the country?

if it's yes you only need to understand how much of the 7.5kva the country uses really, and the place where your can put your line
a generator of 7.5 can be 220v or 380v
most are 220 so monophase, if the country uses a maximun of 4kw you can be able to fire your 1.2 maybe more than 4 but can be a risk,
Just make a phone call to know what is the plug you can use maybe can be a 32amps 220v or sometimes a 63amp 220v. The same if you rent one, if you use a 1.2 it's enough to have a genny 3kw or 5kw like the honda eb6.5 red (5kw) or the honda older ex 5.5 silver (if it's good 4kw)
There are no problem of hurt or blow because the ballasts are very well protected, a problem can be a line loss or frequency loss, if the ballast dont have the proper frequency or voltage can shut down and restrike immediatly several times..... if your 1.2 willdo something like this just shut it down asap because hot restrike can damage the bulb if it's an old one.
But the 1.2 can be powered also through an house circuit...

Leonardo Brocato
Gaffer
Roma Italy

Link to comment
Share on other sites

Hi Guys. I'm gaffering a shoot in a big old country home which itself runs off a 7.5kVA generator. I want to use a 1.2k HMI to try and keep power to a minimum so first question is do I actually need a synchronising crystal generator to ensure I don't "hurt" "blow" the light.

 

It gets a bit more complicated with HMIs because it not only matters what type of HMI ballast you use, but also what type of generator you use. If the OP were using incandescent lights, he could use a AVR type generator (AVR stands for Automatic Voltage Regulator.) However, the harmonic noise that a non-Power Factor Corrected (PFC) electronic HMI ballast will kick back into the power stream can have a severe adverse effect on the power waveform of conventional AVR generators like the Honda EX5500 (the “older EX 5.5 Silver” one Leonardo mentioned.) The harmonic noise these light sources generate will not have nearly as bad an effect on the power supplied by an inverter generator like the Honda EU6500is.

 

As the middle oscilloscope shot below indicates, when you power a standard non-PFC HMI Electronic ballast from a conventional portable generator, the harmonic noise they kick back into the power stream can have a severe adverse effect on the power waveform. Given the large sub-transient impedance of conventional portable generators, even a small degree of harmonic noise being fed back into the power stream will result in a large amount of distortion in its’ voltage.

waveform_elec_ballast.jpg

Left: Grid Power w/ 1.2Kw Arri non-PFC Elec. Ballast. Center: Conventional AVR Power w/ 1.2Kw Arri non-PFC Elec. Ballast. Right: Inverter Power w/ 1.2Kw Arri non-PFC Elec. Ballast.

 

The adverse effects of the harmonic noise exhibited here, can take the form of overheating and failing equipment, circuit breaker trips, excessive current on the neutral wire, and instability of the generator’s voltage and frequency. Harmonic noise of this magnitude can also damage HD digital cinema production equipment, create ground loops, and possibly create radio frequency (RF) interference.

 

When your lighting package consists predominantly of non-linear light sources, like HMI, Fluorescent, & LED lights, it is essential to have Power Factor Correction circuitry (PFC) in the ballasts and to operate them on an inverter generator. The combination of improved power factor and the nearly pure power waveform (1-2 %THD) of a inverter generator creates clean stable set power (like that in the power waveform below right).

wwaveform_PFC-ballast.jpg

Left: Grid Power w/ 1.2Kw P-2-L PFC Elec. Ballast. Center: Conventional AVR Power w/ 1.2Kw P-2-L PFC Elec. Ballast. Right: Inverter Power w/ 1.2Kw P-2-L PFC Elec. Ballast.

 

Chris’s best bet would be to use a 1.2kw HMI with PFC ballast and use an inverter generator like the Honda EU6500is. The Honda EU6500is will also generate less than half the noise of an AVR type generator – making it easier to record clean audio tracks.

 

For more details on what type of generator to use with HMIs and fluorescent lights read the article I wrote for our company news letter on the use of portable generators in motion picture production. The article is available online at http://www.screenlightandgrip. com/html/emailnewsletter_generators.html.

 

Guy Holt, Gaffer, ScreenLight & Grip, Lightng & Grip Rental and Sales in Boston